| Line 495: | Line 495: | ||
===Options and Users=== | ===Options and Users=== | ||
The final area covered by the tutorial is the options and user section. If you are running in authenticated mode and don’t have system privileges then you will not see this section at all and if you are running in un-authenticated mode then no user section will be displayed. | |||
The various options you can specify are displayed in a tabbed dialog with each group of options displayed under a different heading. Each option is displayed with its name, a short description and the current value. You can also click on the ‘?’ link following each description to get a fuller explanation about each option. This is the same as you would get from zmconfig.pl. A number of option groups have a master option near the top which enables or disables the whole group so you should be aware of the state of this before modifying options and expecting them to make any difference. | |||
If you have changed the value of an option you should then ‘save’ it. A number of the option groups will then prompt you to let you know that the option(s) you have changed will require a system restart. This is not done automatically in case you will be changing many values in the same session, however once you have made all of your changes you should restart ZoneMinder as soon as possible. The reason for this is that web and some scripts will pick up the new changes immediately but some of the daemons will still be using the old values and this can lead to data inconsistency or loss. | |||
One of the options you may notice in the ‘System’ tab allows you to specify the default language for your installation of ZoneMinder. Versions 1.17.0 and later support multiple languages but rely on users to assist in creating language files for specific languages. To specify a language you will have to give the applicable code, thus for UK English this is en_gb, and for US English it would be en_us, if no language is given then UK English is assumed. Most languages will be specified in this nn_mm format and to check which languages are available look for files named zm_lang_*.php in the ZoneMinder build directory where the parts represented by the ‘*’ would be what you would enter as a language. This is slightly unwieldy and will probably be improved in future to make it easier to determine language availability. On checking which languages are available it may be that your preferred language is not currently included and if this is the case please consider doing a translation and sending it back to it may be included in future releases. All the language elements are given in the zm_lang_en_gb.php file along with a few notes to help you understand the format. | |||
As mentioned above, you may also see a ‘users’ tab in the Options area. In this section you will see a list of the current users defined on the system. You can also add or delete users from here. It is recommended you do not delete the admin user unless you have created another fully privileged user to take over the same role. Each user is defined with a name and password (which is hidden) as well as an enabled setting which you can use to temporarily enable or disable users, for example a guest user for limited time access. As well as that there is a language setting that allows you to define user specific languages. Setting a language here that is different than the system language will mean that when that user logs in they will have the web interface presented in their own language rather than the system default, if it is available. Specifying a language here is done in the same way as for the system default language described above. | |||
There are also five values that define the user permissions, these are ‘Stream’, ‘Events’, ‘Control’, ‘Monitors’ and ‘System’ Each can have values of ‘None’, ‘View’ or ‘Edit’ apart from ‘Stream’ which has no ‘Edit’ setting. These values cover access to the following areas; ‘Stream’ defines whether a user is allowed to view the ‘live’ video feeds coming from the cameras. You may wish to allow a user to view historical events only in which case this setting should be ‘none’. The ‘Events’ setting determines whether a user can view and modify or delete any retained historical events. The ‘Control’ setting allows you to indicate whether the user is able to control any Pan/Tilt/Zoom type cameras you may have on your system. The ‘Monitors’ setting specifies whether a user can see the current monitor settings and change them. Finally the ‘System’ setting determines whether a user can view or modify the system settings as a whole, such as options and users or controlling the running of the system as a whole. | |||
As well as these settings there is also a ‘Bandwidth’ setting which can be used to limit the maximum bandwidth that a user can view at and a ‘Monitor Ids’ setting that can be used for non-’System’ users to restrict them to only being able to access streams, events or monitors for the given monitors ids as a comma separated list with no spaces. If a user with ‘Monitors’ edit privileges is limited to specific monitors here they will not be able to add or delete monitors but only change the details of those they have access to. If a user has ‘System’ privileges then the ‘Monitors Ids’ setting is ignored and has no effect.’ | |||
That’s pretty much is it for the tour, though there is a lot more to ZoneMinder as you will discover. You should experiment with the various settings to get the results you think are right for your requirements. | |||
==Camera Control== | ==Camera Control== | ||
Revision as of 11:45, 6 September 2007
Please Note: The documentation for ZoneMinder is currently in the process of being migrated to this Wiki. The documents present in the distribution and available from the Documentation page on the main site should be used until such time as this notice is removed.
Introduction
A while back my garage was burgled and all my power tools were stolen! I realised shortly after that if I'd just had a camera overlooking the door then at least I'd have know exactly when and who did the dirty deed. And so ZoneMinder was born. It's still relatively new but hopefully it has developed to be something that can be genuinely useful and prevent similar incidents or even perhaps bring some perpetrators to justice.
As well as being fast ZoneMinder is designed to be friendly and even more than that, actually useful. As well as the fast video interface core it also comes with a user friendly and comprehensive PHP based web interface allowing you to control and monitor your cameras from home or even at work or on the road. It supports variable web capabilities based on available bandwidth. The web interface also allows you to view events that your cameras have captured and archive them or review them time and again, or delete the ones you no longer wish to keep. The web pages directly interact with the core daemons ensuring full co-operation at all times. ZoneMinder can even be installed as a system service ensuring it is right there if your computer has to reboot for any reason.
Requirements
ZoneMinder needs a couple of things to work. Ordinarily the ‘configure’ script will check for the presence of required (and optional) components but it is useful to be prepared beforehand.
Firstly, it uses MySQL so you'll need that. In order to compile you need to make sure you have a development installation and not just a runtime; this is because it needs to use the MySQL header files. If you are running an RPM based distribution then it’s probably worth installing all the pure mysql rpm files to be sure you have the right ones.
Finally, there is quite a bit of image streaming in the package. So if you don't have FireFox or another browser that supports image streaming natively I recommend you get the excellent Cambozola java applet from http://www.charliemouse.com/code/cambozola/ which will let you view the image stream in Internet Explorer and others. Otherwise you're limited to just refreshing still images or mpeg based streams, if you have compatible plugins.
Hardware-wise, ZoneMinder has been used with various video and USB cameras with the V4L interface. It will also work with most Network or IP cameras. I don't have a lot of cameras myself so I've not had change to test it with a huge range personally however there is a list of devices that are definitely known to work on the web site. Please enter you camera on the Wiki list on zoneminder.com if your camera works and is not listed. You do need to have Video4Linux installed. In terms of computer hardware, there are no hard and fast requirements. You may get a system that works with one or two cameras going on an old P200 but you will be able to support more cameras, at a higher frame rate, with faster machines with more RAM. More guidance is available on the web forums.
Components
- zmc
- zma
- zmf
- zms
- zmu
- zmfix
- This is a small binary that exists only to ensure that the video device files can be read by the main capture daemons. It is often the case that these device files are set to be accessible by root only on boot. This binary runs setuid and ensures that they have appropriate permissions. This is not a daemon and runs only on system start and then exits.
- zmpkg.pl
- zmdc.pl
- zmfilter.pl
- zmaudit.pl
- zmwatch.pl
- zmupdate.pl
- zmvideo.pl
- zmx10.pl
- zmtrigger.pl
- zmcontrol-*.pl
- zmtrack.pl
- zm
- ZoneMinder.pm
- ZoneMinder/Base.pm
- ZoneMinder/Config.pm
- ZoneMinder/Debug. pm
- ZoneMinder/Database.pm
- ZoneMinder/SharedMem.pm
- ZoneMinder/ConfigAdmin.pm
- ZoneMinder/Trigger/*.pm
Building
There are also two further parameters you can add if your web user and group are not both 'apache'. These are --with-webuser and --with-webgroup.
This is also when you have the opportunity to pass any additional flags to the compiler to modify how the application is built. To do this append CFLAGS=”<options>” and CXXFLAGS=”<options>” to pass in compiler flags for ‘c’ and ‘c++’ compilation respectively. For instance the default compiler flags are usually –O2 and –g to create binaries with moderate optimisation and debugging symbols. If you wanted to optimise further, including processor specific tweaks but still keep debugging symbols then could use CFLAGS="-g -O3 -march=pentium4" and CXXFLAGS="-g -O3 -march=pentium4" for instance. Consult the gcc/g++ documentation for help on these and other options. Also be aware that even if you optimise your ZoneMinder build, any libraries that get linked in will only perform as well as the options used when they were built allows. Thus to get full benefit you would usually need to rebuild libjpeg.a and/or other libraries with similar options.
Type
./configure –help
Installation
Installation from Source
For a new installation the next thing you will need to do is create your database and database users. So type the commands as follows,
mysql mysql < db/zm_create.sql
mysql mysql
grant select,insert,update,delete on <database name>.* to '<database user>'@localhost identified by '<database password>';
quit
mysqladmin reload
You may need to supply a username and password to the mysql commands in the first place to give yourself sufficient privileges to perform the required commands. If you want to host your database on a different machine than that which ZoneMinder is running on then you will need to perform this step on the remote machine and reference the ZoneMinder machine instead of localhost. If you are running remote databases you probably already know all this, if you are not then don’t worry about it!
At this stage typing
make install
chkconfig --add zm
zmpkg.pl start
make uninstall
Installation from RPM
Fedora Core: /usr/share/doc/zm-{version number}
Mandrake:
Fedora Core: /etc/httpd/conf.d/zm.conf
Mandrake:
vi /etc/zm.conf
service mysqld start
/usr/lib/zm/bin/zminit
chkconfig –levels 35 httpd on
service httpd start
service zm start
Upgrading
Upgrading from Source
make install
The next step in an upgrade is to run the zmupgrade.pl script to make any changes to the database or file system required by the new version. Ordinarily you can run this from your ZoneMinder build directory by doing
zmupdate.pl –version=<from version> [--user=<database user> --pass=<database password>]
mysql < zm-1.21.4.dump
for example.
Tutorial
Defining Monitors
To help you get started on the video configuration the best thing is to use a tool like 'xawtv' (http://bytesex.org/xawtv/) to get a picture you're happy with, and to check your camera works. Please note that just because you can see a video stream in these tools does not necessarily guarantee that your camera will work with ZoneMinder. This is because most tools just ‘map’ the video image through onto screen memory transparently without intercepting it, whereas ZoneMinder needs to capture the image and, usually, inspect it. This is called frame grabbing and to check it you should use the facility in xawtv, or other tool, to capture either one or more still images or possibly a movie. If this works and the images or movie are not garbage then the chances are that ZoneMinder will work fine also.
Once you have validated your camera run 'zmu -d <device_path> -q -v' to get a dump of the settings (note, you will have to additionally supply a username and password to zmu if you are running in authenticated mode). You can then enter these values into the video related options of the monitor configuration panel. The 'device_path' referred to here is the path to your video device file, for instance /dev/video0 etc. If 'zmu' gives you an error related to permissions run 'zmfix -a' to make sure you can access all the video devices.
Monitor Tab
- Name
- Source Type
- This determines whether the camera is a local one attached to a physical video or USB port on your machine, a remote network camera or an image source that is represented by a file (for instance periodically downloaded from a alternate location). Choosing one or the other affects which set of options are shown in the next tab.
- Function
- None – The monitor is currently disabled and no streams can be viewed or events generated.
- Monitor – The monitor will only stream feeds but no image analysis is done and so no alarms or events will be generated,
- Modect – or MOtion DEteCTtion. All captured images will be analysed and events generated where motion is detected.
- Record – In this case continuous events of a fixed length are generated regardless of motion which is analogous to a convention time-lapse video recorder. No motion detection takes place in this mode.
- Mocord – This is a hybrid of Modect and Record and results in both fixed length events being recorded and also any motion being highlighted within those events.
- Generally speaking it is best to choose ‘Monitor’ as an initial setting here..
- Enabled
- The enabled field indicates whether the monitor should be started in an active mode or in a more passive state. You will nearly always want to check this box, the only exceptions being when you want the camera to be enabled or disabled by external triggers or scripts. If not enabled then the monitor will not create any events in response ot motion or any other triggers.
- Linked Monitors
- This field allows you to select other monitors on your system that act as triggers for this monitor. So if you have a camera covering one aspect of your property you can force all cameras to record while that camera detects motion or other events. You can either directly enter a comma separated list of monitor ids or click on ‘Select’ to choose a selection. Be very careful not to create circular dependencies with this feature however you will have infinitely persisting alarms which is almost certainly not what you want!
- Maximum FPS
- On some occasions you may have one or more cameras capable of high capture rates but find that you generally do not require this performance at all times and would prefer to lighten the load on your server. This option permits you to limit the maximum capture rate to a specified value. This may allow you to have more cameras supported on your system by reducing the CPU load or to allocate video bandwidth unevenly between cameras sharing the same video device. This value is only a rough guide and the lower the value you set the less close the actual FPS may approach it especially on shared devices where it can be difficult to synchronise two or more different capture rates precisely. This option controls the maximum FPS in the circumstance where no alarm is occurring only.
- Alarm Maximum FPS
- Reference Image Blend %ge
- Triggers
Source Tab (local device)
- Device Path/Channel
- Enter the full path to the device file that your camera is attached to, e.g. /dev/video0. Some video devices, e.g. BTTV cards support multiple cameras on one device so in this case enter the channel number in the Channel box or leave it at zero if you're using a USB camera or one with just one channel.
- Device Format
- Capture Palette
- Capture Width/Height
- The dimensions of the video stream your camera will supply. If your camera supports several just enter the one you'll want to use for this application, you can always change it later. However I would recommend starting with no larger than 320x240 or 352x288 and then perhaps increasing and seeing how performance is affected. This size should be adequate in most cases. Some cameras are quite choosy about the sizes you can use here so unusual sizes such as 197x333 should be avoided initially.
- Orientation
Source Tab (remote device)
- Remote Host/Port/Path
- Use these fields to enter the full URL of the camera. Basically if your camera is at http://camserver.home.net:8192/cameras/camera1.jpg then these fields will be camserver.home.net, 8192 and /cameras/camera1.jopg respectively. Leave the port at 80 if there is no special port required. If you require authentication to access your camera then add this onto the host name in the form <username>:<password>@<hostname>.com. This will usually be 24 bit colour even if the image looks black and white.
- Remote Image Colours
- As per local devices.
- Orientation
Source Tab (file device)
- File Path
- File Colours
- Orientation
Timestamp Tab
- Timestamp Label Format
- This relates to the timestamp that is applied to each frame. It is a ‘strftime’ style string. It is actually passed through strftime and then through printf to add the monitor name so a format of '%%s - %y/%m/%d %H:%M:%S' (note the double % at the beginning) would be recommended though you can modify it if necessary. If you don’t want a timestamp or have a camera that puts one on itself then leave this field blank. If you add a second %%s placeholder in the string this will be filled by any of the ‘show text’ detailed in the zmtriggers.pl section.
- Timestamp Label X/Y
Buffers Tab
- Image Buffer Size
- Warm-up Frames
- Pre/Post Event Image Buffer
- Alarm Frame Count
Control Tab
- Controllable
- Control Type
- Control Device
- Control Address
- This is the address of your camera. Some control protocols require that each camera is identified by a particular, usually numeric id. If your camera uses addressing then enter the id of your camera here. If your camera is a network camera then you will usually need to enter the hostname or IP address of it here. This is ordinarily the same as that given for the camera itself.
- Auto Stop Timeout
- Track Motion
- Track Delay
- Return Location
- Return Delay
X10 Tab
- X10 Activation String
- X10 Input Alarm String
- X10 Output Alarm String
Misc Tab
- Event Prefix
- Section Length
- Frame Skip
- FPS Report Interval
- Default Scale
- Web Colour
Defining Zones
The Zone view is split into two main areas, on the left is the options are area and on the right is the zone drawing area. A default or new zone will cover the whole drawing area and will overlay any other zones you already have on there. Unlike the previous zones image, the current zone is coloured green, other zones will be orange regardless of type. Your first task is to decide if you want the zone over the whole image or whether you can narrow down the detection area; the smaller the zone, the less processing time it takes to examine it. If you wish to the edit the dimensions of the zone you can either manually fill in the table containing the zone points under the image, or click on the zone corners once to select it (it should turn red), and then click on the desired location to relocate it. Moving your mouse over a point will highlight the corresponding entry in the points table and vice versa.
- Name
- This is just a label to identify the zone by. You can change this to be more representative if you like, though it isn't used much except for logging and debugging.
- Type
- This is one of the more important concepts in ZoneMinder and there are five to choose from.
- Active - This is the zone type you'll use most often, and which will be set for your default zone. This means that this zone will trigger an alarm on any events that occur within it that meet the selection criteria.
- Inclusive - This zone type can be used for any zones that you want to trigger an alarm only if at least one other Active zone has already triggered one. This might be for example to cover an area of the image like a plant or tree which moves a lot and which would trigger lots of alarms. Perhaps this is behind an area you'd like to monitor though, in this case you'd create an active zone covering the non-moving parts and an inclusive zone covering the tree perhaps with less sensitive detection settings also. If something triggered an alarm in the Active zone and also in the Inclusive zone they would both be registered and the resulting alarm would be that much bigger than if you had blanked it out altogether.
- Exclusive - The next zone Type is Exclusive. This means that alarms will only be triggered in this zone if no alarms have already been triggered in Active zones. This is the most specialised of the zone types and you may never use it but in its place it is very useful. For instance in the camera covering my garden I keep watch for a hedgehog that visits most nights and scoffs the food out of my cats bowls. By creating a sensitive Exclusive zone in that area I can ensure that a hedgehog alarm will only trigger if there is activity in that small area. If something much bigger occurs, like someone walking by it will trigger a regular alarm and not one from the Exclusive zone. Thus I can ensure I get alarms for big events and also special small events but not the noise in between.
- Preclusive - This zone type is relatively recent. It is called a Preclusive zone because if it is triggered it actually precludes an alarm being generated for that image frame. So motion or other changes that occur in a Preclusive zone will have the effect of ensuring that no alarm occurs at all. The application for this zone type is primarily as a shortcut for detecting general large-scale lighting or other changes. Generally this may be achieved by limiting the maximum number of alarm pixels or other measure in an Active zone. However in some cases that zone may cover an area where the area of variable illumination occurs in different places as the sun and/or shadows move and it thus may be difficult to come up with general values. Additionally, if the sun comes out rapidly then although the initial change may be ignored in this way as the reference image catches up an alarm may ultimately be triggered as the image becomes less different. Using one or more Preclusive zones offers a different approach. Preclusive zones are designed to be fairly small, even just a few pixels across, with quite low alarm thresholds. They should be situated in areas of the image that are less likely to have motion occur such as high on a wall or in a corner. Should a general illumination change occur they would be triggered at least as early as any Active zones and prevent any other zones from generating an alarm. Obviously careful placement is required to ensure that they do not cancel any genuine alarms or that they are not so close together that any motion just hops from one Preclusive zone to another. As always, the best way is to experiment a little and see what works for you.
- Inactive - This final zone type is the opposite of Active. In this zone type no alarms will ever be reported. You can create an Inactive zone to cover any areas in which nothing notable will ever happen or where you get constant false alarms that don't relate to what you are trying to monitor. An Inactive zone can overlay other zone types and will be processed first.
- It was mentioned above that Inactive zones may be overlaid on other zones to blank out areas however as a general principle you should try and make zones abut each other as much as possible and not overlap. This helps avoid repeated duplicate processing of the same area. For instance an Inclusive zone overlaying an Active zone when all other settings are the same will always trigger when the Active zone does which somewhat defeats the object of the exercise. One exception to this is Preclusive zones. These may be situated within Active areas are they are processed first and if small may actually save processing time by preventing full analysis of the image.
- Presets
- This contains a predefined list of some common zone settings. Selecting one will fill in some of the other fields in the page and help you to pick appropriate values for your zones. Note that it may be that none of the presets will be appropriate for your purposes so it is worth going through the individual options below to ensure that each has a sensible value.
- Units
- This setting which details whether certain of the following settings are in Pixels or Percent, where ‘Percent’ refers to a percentage area of the zone itself. In general ‘Pixels’ is more precise whereas percentages are easier to use to start with or if you change image sizes frequently. If you change this setting all appropriate values below are redisplayed in the correct context. A good tip would be to initially enter the settings in Percent and then change to Pixels if you wish to be more precise. Be aware though that repeated flipping between the settings may cause rounding errors. Note, the sense of the percentage values refers to the area of the zone and not the image as a whole. This makes trying to work out necessary sizes rather easier.
- Alarm Colour
- The option after that allows you to specify what colour you'd like any alarms this zone generates to be highlighted on images. Pick anything you like that will show up against your normal image background. This option is irrelevant for Preclusive and Inactive zones and will be disabled. For Inactive zones all subsequent options are likewise disabled.
- Alarm Check Method
- This setting allows you to specify the nature of the alarm checking that will take place, and more specifically what tests are applied to determine whether a frame represents an alarm or not. The three options are ‘AlarmPixels’, ‘FilteredPixels’ and ‘Blobs’ and depending on which option is chosen some of the following other settings may become unavailable. The first of these indicates that only a count of individual alarmed pixels should be used to determine the state of a image, the second indicate that the pixels should be filtered to remove isolated pixels (see below) before being counted, and the third uses a more sophisticated analysis which is designed to aggregate alarmed pixels into continuous groups, or ‘blobs’. Blob analysis default, however this method takes slightly longer and so if you find that one of the other methods works just as well for you and you wish to maximise performance you can opt for that instead. Some of the more useful alarm related features such as highlighted analysis images are only available with the ‘Blob’ setting.
- Min/Maximum Pixel Threshold
- These setting are used to define limits for the difference in value between a pixel and its predecessor in the reference image. For greyscale images this is simple but for colour images the colours are averaged first, originally this used an RMS (root mean squared) algorithm but calculating square roots mugs performance and does not seem to improve detection. Using an average means that subtle colour changes without any brightness change may go undetected but this is not the normal circumstance. There is also the option to use a more sophisticated integer algorithm to calculate a Y (or brightness) value from the colours themselves.
- Filter Width/Height
- To improve detection of valid event ZoneMinder applies several other functions to the data to improve its ability to distinguish interesting signals from uninteresting noise. The first of these is a filter that removes any pixels that do not participate in a contiguous block of pixels above a certain size. :These options are always expressed in pixels and should be fairly small, and an odd number, three or five is a good value to choose initially. Application of this filter removes any tiny or discontinuous pixels that don't form part of a discrete block.
- Zone Area
- This field differs from the others in that it may not be written to. It is there purely as a useful reference, when working in pixel units, of the area of the zone.
- Min/Maximum Alarmed Area
- The following two settings define the minimum and maximum number of pixels that exceed this threshold that would cause an alarm. If the units are Percent this (and following options) refers to the percentage of the frame and not the zone, this is so these values can be related between zones. The minimum value must be matched or exceeded for an alarm to be generated whereas the maximum must not be exceeded or the alarm will be cancelled. This is to allow for sudden changes such as lights coming on etc, which you may wish to disregard. In general a value of zero for any of these settings causes that value to be ignored, so you can safely set a maximum to zero and it will not be used. The use of just a number of pixels is however a very brute force method of detection as many small events dispersed widely are not distinguished from a compact one.
- Min/Maximum Filtered Area
- These are two additional bounds that specify the limits of pixels that would cause an alarm after this filtering process. As the filtering process can only remove alarmed pixels it makes no sense for the Minimum and Maximum Filtered Area to be larger than the equivalent Alarmed Area and in general they should be smaller or the same.
- Min/Maximum Blob Area
- The next step in the analysis phase is the collation of any remaining alarmed areas into contiguous blobs. This process parses the image and forms any pixels that adjoin other alarmed pixels into one or more larger blobs. These blobs may be any shape and can be as large as the zone itself or as small as the filtered size. The Minimum and Maximum Blob Size settings allow you to define limits within which an alarm will be generated. Of these only the Minimum is likely to be very useful.
- Min/Maximum Blobs
- Finally the Minimum and Maximum Blobs settings specify the limits of the actual number of blobs detected. If an image change satisfies all these requirements it starts or continues an alarm event.
Viewing Monitors
Controlling Monitors
Filtering Events
- %EI% Id of the event
- %EN% Name of the event
- %EC% Cause of the event
- %ED% Event description
- %ET% Time of the event
- %EL% Length of the event
- %EP% Path to the event
- %MN% Name of the monitor
Viewing Events
Options and Users
