(51 intermediate revisions by 2 users not shown)
==About==
/usr/bin/zmtrigger.pl (debian location) is an optional program for Zoneminder that listens on the network for commands. Read the perl script for more information. It is a telnet or TCP server.
It can be used in different ways.
'''1)''' It can be used is to overlay text information (e.g. temperature sensor) onto the video feed.
One way it can be used is to overlay text information from an external source (e.g. temperature sensor) onto the video feed. It can also be used as an external trigger source for cameras. By using an external trigger source, you can avoid some of the problems inherent in ZM modect - false alarms, and CPU use. False alarms are commonly caused when the video feed has a change come across it, such as weather events, wildlife, or the transition from daylight filter to night ir filter. An external trigger source might be one or more of a PIR, Microwave, or Ultrasonic sensor.
'''2)''' It can also be used as an external trigger / alarm source for cameras. By using an external alarm, you can avoid some of the problems inherent in ZM software modect - false alarms, and CPU usage. False alarms are commonly caused when the video feed has an ambient change come across it, e.g. weather events, wildlife, or the transition from daylight to night ir filter.
Note that if you have a house, or single breaker, you might want to consider using [[X10]] for Zoneminder. This will save you the need for ethernet wiring, or setting up wifi.
'''3)''' You can monitor which alarms are active or not at a given time. ZMTrigger reports when alarms are active, and when they are closed. This data can be queried by external programs.
'''4)''' It can be used as a standalone alarm system. In this scenario, you would not have cameras, and instead only have devices that send TCP packets to the ZMTrigger daemon. For example, you might install a motion sensor using [[Arduino]] and then have it report to the ZM server.
Some notes on ZMTrigger from the official docs here: https://zoneminder.readthedocs.io/en/stable/userguide/components.html
==Configuration==
==Configuration==
Enable it first, by going into options, config, and checking Enable Triggers (OPT_TRIGGER).
Then
<pre># service restart zoneminder</pre>
Then restart ZM.
# /etc/init.d/zoneminder restart
Verify it is running with
<pre>ps auxw | grep zmtrigger</pre>
Verify the port is 6802 and tcp
netstat -ntulp
or
ss -ntulp
Make sure no firewall is blocking it on port 6802.
iptables -L
or
nft list tables
nft list table <result of previous command>
==Usage==
==Usage==
Line 38: Line 52:
then press return.
then press return.
Refer to [[Documentation]] for what this command means. A brief explanation for this is: <pre>MonitorID # | Show text mode |||| text to put in.</pre>
Alternatively, you can run a one line command with your choice of program to send a tcp packet. Such as: [https://forums.zoneminder.com/viewtopic.php?p=140425]
printf '6|on|1|motion||||\n' | socat - TCP:127.0.0.1:6802
Refer to the [https://zoneminder.readthedocs.io/en/stable/userguide/components.html Official Docs] or the zmtrigger.pl script for what this command means. A brief explanation for this is: <pre>MonitorID # | Show text mode |||| text to put in.</pre>
Line 44: Line 62:
For more examples and scripts of ZMTrigger search the [https://forums.zoneminder.com forums].
====Example Script====
Note: You can also send this to telnet in a shell script via:
#!/bin/bash
# call script and pass monitor number
# e.g.
# "$ ./telnet_zmtrigger_test.sh 12"
# fields are:
# B<id>|B<action>|B<score>|B<cause>|B<text>|B<showtext>
IPADDRESSOFZMSRV=192.168.1.178
telnet $IPADDRESS 6802 <<EOF
$1|on+3|10|ZMTEST||
EOF
Here is a script of connecting to an ipaddress that serves a value from a sensor.
====Example Setup====
Here is a script that connects to an ipaddress which serves a sensor value.
Wget is not as fast as possible, but this is simple and works quickly as a test.
Line 87: Line 122:
* Less false positives
* Less CPU usage
* Less CPU usage
* No zone configuration required
Some drawbacks
Some drawbacks
* Some assembly required
* Probably more difficult than software motion detection built into ZM
* Zone configuration isn't necessary, but you may have to install these, which is slow and requires fish tape, drywall saw, experience with installing an ethernet or electrical outlet, etc...
====Types of Controllers====
[[File:ArduinoUno.jpg|thumb|right|upright=0.5|alt=Uno||Arduino Uno DIP]]
[[File:ArduinoUno.jpg|thumb|right|upright=0.5|alt=Uno||Arduino Uno. Note that you may get lower power usage with other options such as a Nano or Pro Micro.]]
This is up to you. If you have a wired ethernet connection available for the external sensor, then an Arduino Uno is a good choice. If you don't want to run ethernet, then an ESP8266 or Arduino w/wifi should do. An Arduino Uno will require a separate ethernet board.
This is up to you. If you have a wired ethernet connection available for the external sensor, then an [[Arduino]] Uno is a good choice. If you don't want to run ethernet, then an ESP8266 or Arduino w/wifi should do. An Arduino Uno will require a separate ethernet board. You can also connect an Arduino via USB, if the computer is within 15 feet.
====Types of Sensors====
You will need to decide which sensors to use. There are many options. I'll start with the common options, most likely to be used by a casual hacker. The first obvious options for Arduino solutions would be a PIR sensor, a Microwave sensor, or an Ultrasonic sensor.
You will need to decide which sensors to use. There are many options. This is what I've used.
=====PIR Sensors=====
Line 106: Line 142:
* Range is limited to 10-20 Feet. Sensitivity can be tuned.
* Sunlight will cause false triggers. Direct OR indirect.
* Sunlight will cause false triggers. Direct OR indirect. Software or hardware may be able to mitigate this (TODO).
* Works good in a hallway, or room where no outdoor sunlight will penetrate.
Overall, the PIR Sensors are good if you have the right environment. They are not feasible outside, but indoors, away from sunlight, they do the trick.
=====Microwave Sensors=====
[[File:hb100.jpeg|frame|HB100 10GHz Microwave module without circuitry||HB100]]
Microwave sensors operate in the 10-24GHz radio bands. The 10 GHz sensors have a range of about 20-30 feet for a person, more for large vehicles (reflective metal objects). The 24GHz sensors have shorter range. There are a variety of these, from brand name, to cheap. HB100 is a common 10GHz model, though it requires an external amplifier to read the uV signal. This can be as simple as an lm386 arduino module. Other sensors have [https://www.parallax.com/product/32213 circuitry built in] to output a high or low signal depending on the motion, and how sensitive you make it. These sensors are a step above the PIR in some ways, but have their own limitations.
Microwave sensors operate in the 5-24GHz radio bands. The 10 GHz sensors have a range of about 20-30 feet for a person, more for large vehicles (reflective metal objects). The 24GHz sensors have shorter range. There are a variety of these, from brand name, to cheap. The best sensor currently available at the lowest price is the HFS-DC06H.
* Relatively short range for radio. Typically 10M, but some claim 15M. Depends on how conductive the item in motion is.
* Relatively short range for radio. Depends on RF frequency, but typically you get 5GHz = 10M, 10GHz = 5M, 24GHz = <3M
* Can't use multiple of these, as they may interfere with each other. (need to test)
* Some of these can interfere with each other (some do not, depends on model).
* Items are detected greater when moving towards or away the sensor, not as much when moving across its field of sight.
* Detection of items depends on conductivity (large metal objects such as cars are detected from a larger distance than people. This is expected).
* May work too well - Mice can set off alarms (not false, but essentially unwanted alarms)(sensitivity can usually be adjusted).
'''Why don't I make a radio sensor that goes longer than 10M?'''
[https://github.com/Ttl/fmcw It's been done]. And if they are within the ISM bands they can be used without FCC testing. More details here: [https://hackaday.com/2014/02/24/guest-post-try-radar-for-your-next-project/ make FMCW radars].  Not easy but doable. The trick will be to make one that is practical enough but also not $100 each.
[https://github.com/Ttl/fmcw It's been done]. And if they are within the ISM bands they can be used without FCC testing and approval. More details here: [https://hackaday.com/2014/02/24/guest-post-try-radar-for-your-next-project/ make FMCW radars].  Not easy but doable. The trick will be to make one that is practical enough but also not $100 each.
=====Ultrasonic Sensors=====
I have not and will not use ultrasonic sensors, but maybe someone else has some experience they can chime in with here (no pun intended).
I do not use ultrasonic sensors, but maybe someone else has some experience they can chime in with here (no pun intended).
* Uses high frequency sound, may disrupt animals.
Line 132: Line 169:
=====Infrared Trip Sensors=====
It's easy to find infrared trip sensors (think a laser going from 10-50 feet across). These can be setup with a microcontroller, and if someone walks across the beam, you can activate the alarm. Some brands are [http://www.sick.com/us/en Sick] or Seco-larm Enforcer. If you need a real short IR (inches), off the shelf Arduino modules will work (ir photo beam detector). These can be purchased from distributors such as [http://www.allelectronics.com] and others online. Search the opto-electronics section (subject to change).
It's easy to find infrared trip sensors (think a laser going from 10-50 feet across). These can be setup with a microcontroller, and if someone walks across the beam, you can activate the alarm. Some brands are [http://www.sick.com/us/en Sick] or Seco-larm Enforcer. If you need a real short IR (inches), off the shelf Arduino modules will work (ir photo beam detector). These can be purchased from distributors such as [http://www.allelectronics.com] and others online. Search the opto-electronics section (subject to change). Buy used if you are on a budget.
* Requires a bit of installation, though works well, when installed.
* Requires power at both ends of the laser.
* More Immune to sun interference than PIR
* One end must connect back to server somehow (ethernet/wifi)
* One end must connect back to server somehow (ethernet/wifi/usb/X10)
* Reasonably long distance. Some are up to 100M.
* Possible to avoid if you step over them. Put these aiming at a device that moves such as a door or gate.
* Possible to avoid if you step over them. Put these aiming at a device that moves such as a door or gate. You can also get larger sensors, which can be a 6-7 feet tall, and are used in elevators to detect people in the doorway (search "[https://www.pepperl-fuchs.com/global/en/classid_104.htm elevator door sensors]").
* These are all in the class of "photo electric sensors"
* the single beam modules (that don't have a receiver) may require a reflective sticker (bike reflector) on the other side
An example sketch is included in the links at the bottom.
=====Inductive Sensors=====
There are products that, similar to capacitive sensors, (think a Theremin https://en.wikipedia.org/wiki/theremin) you can for example attach a wire to a doorknob (or any piece of metal), then when someone touches the other side of the doorknob, the alarm is set off. These can be purchased on eBay advertised as "120db Wireless Touch Sensor Security Alarm Loud Door Knob" or some variation thereof, with even a loud buzzer should room service try to enter your room (oops).
[[File:Hotel_door_alarm.jpg|400px|thumb|right|For security purposes, tracking contact on any piece of metal is easy.]]
=====Other Sensors=====
An infinite amount of devices could be used as triggers. House alarms use reed switches on windows and doors. Laser diodes could be used across long distances. If you have the capital, then there are many off the shelf products that can be purchased.
==Troubleshooting==
==Troubleshooting==
Line 172: Line 215:
This means you could have multiple sensors, each triggering a different location. A reed switch on a window, a laser
on a door, etc... When the alarm goes off, the video feed displays the alarm that was triggered.
* "Can I have these arduino sketches set off multiple cameras?" Yes. You can edit the Arduino sketch to send more packets, or "link monitors" in Zoneminder. Two approaches (the latter is easier). https://forums.zoneminder.com/viewtopic.php?f=36&t=26794
* If using an ethernet or wifi based device, you will want to consider low power modes. For example, on the ENC28J60, it is possible to include https://github.com/UIPEthernet/UIPEthernet/blob/master/utility/Enc28J60Network.cpp (this is a seperate library, from UIPEthernet) and call the Enc28J60Network::powerOff(void) command to save about 2 watts (from 3 watts to 1).
== See Also ==
== See Also ==
* [[How to use your external camera's motion detection with ZM]]
* [[How to use your external camera's motion detection with ZM]] - A good writeup on ZMTrigger from the original developer of ZMNinja
* https://sparxeng.com/blog/software/zoneminder-network-triggering - More explanations
* [https://forums.zoneminder.com/viewtopic.php?f=36&t=25704 ZM Forums: Add temperature to image]
Line 181: Line 230:
* [[Dedicated SBC Camera Monitor]]
*Arduino Infrared Tripwire Sketch via ethernet: [https://notabug.org/monitor/ZMHW_Project_LaserDiodeSensor] alternative mirror: [https://git.steakelectronics.com/adminguy/ZMHW_Project_LaserDiodeSensor]
* Arduino Infrared Tripwire Sketch via ethernet: [https://forums.zoneminder.com/viewtopic.php?f=9&t=27442]
* Arduino Sketch via USB [https://forums.zoneminder.com/viewtopic.php?f=9&t=26945]
* [[Arduino]]
[[Category:Dummies_Guide]]
Latest revision as of 15:52, 24 August 2026
1) It can be used is to overlay text information (e.g. temperature sensor) onto the video feed.
4) It can be used as a standalone alarm system. In this scenario, you would not have cameras, and instead only have devices that send TCP packets to the ZMTrigger daemon. For example, you might install a motion sensor using Arduino and then have it report to the ZM server.
Configuration
Then restart ZM.
netstat -ntulp
or
ss -ntulp
iptables -L
or
nft list tables
Usage
Then type in another terminal
telnet ipaddress 6802
1|show||||testingOSD
then press return.
Alternatively, you can run a one line command with your choice of program to send a tcp packet. Such as: [1]
Refer to the Official Docs or the zmtrigger.pl script for what this command means. A brief explanation for this is:
#!/bin/bash
# e.g.
# fields are:
$1|on+3|10|ZMTEST||
EOF
Example Setup
#!/bin/bash
counter=1
while [$counter -le 10]
do
PRESSURE=`wget ipaddress -q -O -`
echo "1|show||||$PRESSURE" | telnet ipaddress 6802
sleep 4
#((counter++))
done
Possible uses of text trigger
  • temperature
  • air pressure
  • humidity
  • sunset/sunrise time
  • which alarm activated
  • which person entered an electronically locked door
  • random quote / message
  • id of last camera alarm that went off on system
  • the name of the person buying something from the POS system
  • insert idea here
As an External Trigger
Some benefits
  • Fully customizable
  • Less false positives
  • Less CPU usage
  • No zone configuration required
Some drawbacks
  • Some assembly required
  • Zone configuration isn't necessary, but you may have to install these, which is slow and requires fish tape, drywall saw, experience with installing an ethernet or electrical outlet, etc...
Uno
Types of Sensors
PIR Sensors
  • Range is limited to 10-20 Feet. Sensitivity can be tuned.
  • Sunlight will cause false triggers. Direct OR indirect. Software or hardware may be able to mitigate this (TODO).
  • Works good in a hallway, or room where no outdoor sunlight will penetrate.
Microwave Sensors
HB100
  • Relatively short range for radio. Depends on RF frequency, but typically you get 5GHz = 10M, 10GHz = 5M, 24GHz = <3M
  • Some of these can interfere with each other (some do not, depends on model).
  • Detection of items depends on conductivity (large metal objects such as cars are detected from a larger distance than people. This is expected).
  • May work too well - Mice can set off alarms (not false, but essentially unwanted alarms)(sensitivity can usually be adjusted).
Ultrasonic Sensors
  • Uses high frequency sound, may disrupt animals.
It's easy to find infrared trip sensors (think a laser going from 10-50 feet across). These can be setup with a microcontroller, and if someone walks across the beam, you can activate the alarm. Some brands are Sick or Seco-larm Enforcer. If you need a real short IR (inches), off the shelf Arduino modules will work (ir photo beam detector). These can be purchased from distributors such as [2] and others online. Search the opto-electronics section (subject to change). Buy used if you are on a budget.
  • Requires a bit of installation, though works well, when installed.
  • Requires power at both ends of the laser.
  • More Immune to sun interference than PIR
  • One end must connect back to server somehow (ethernet/wifi/usb/X10)
  • Reasonably long distance. Some are up to 100M.
  • Possible to avoid if you step over them. Put these aiming at a device that moves such as a door or gate. You can also get larger sensors, which can be a 6-7 feet tall, and are used in elevators to detect people in the doorway (search "elevator door sensors").
  • These are all in the class of "photo electric sensors"
  • the single beam modules (that don't have a receiver) may require a reflective sticker (bike reflector) on the other side
Inductive Sensors
Other Sensors
tail -f  /var/log/zm/zmtrigger.log
The default wait timeout is 8 hours for MySQL. The solution seems to be add a wait_timeout >300, or use the default. Note that this might be fixed for ZM > 1.30.4 Reference:[3]
  • Arduino Infrared Tripwire Sketch via ethernet: [4]
  • Arduino Sketch via USB [5]