Line 28: Line 28:
PURGE BY AGE
PURGE BY AGE
Creating a new filter with a 'date/time' set to 'greater than' and a value of '+169' with 'Delete All Matches' ticked will clear all events over 7 days old (by hours - the event in the first hour is actually +2!)
Creating a new filter with a 'date/time' set to 'greater than' and a value of '+169' with 'Delete All Matches' ticked will clear all events over 7 days old (by hours - the event in the first hour is actually +2 ! - is that because of daylight saving?)
Save this with 'Run Filter In Background' checked to have it run automatically.
Revision as of 12:13, 17 September 2013
The filter is called PurgeWhenFull and to find it, choose one of the event counts from the console page, for instance events in the last hour, for one of your monitors.
In the filter window there is a drop down select box labeled 'Use Filter', that lets your select a saved filter. Select 'PurgeWhenFull' and it will load that filter.
Check the zmfilter.log file to make sure it is running as sometimes missing perl modules mean that it never runs but people don't always realize.
There are two methods for ZM to remove files when they are deleted that can be found in Options under the System tab ZM_OPT_FAST_DELETE and ZM_RUN_AUDIT.
PURGE BY AGE
Creating a new filter with a 'date/time' set to 'greater than' and a value of '+169' with 'Delete All Matches' ticked will clear all events over 7 days old (by hours - the event in the first hour is actually +2 ! - is that because of daylight saving?) Save this with 'Run Filter In Background' checked to have it run automatically.
ZM_OPT_FAST_DELETE:
Normally an event created as the result of an alarm consists of entries in one or more database tables plus the various files associated with it. When deleting events in the browser it can take a long time to remove all of this if your are trying to do a lot of events at once. It is recommended that you set this option which means that the browser client only deletes the key entries in the events table, which means the events will no longer appear in the listing, and leaves the zmaudit daemon to clear up the rest later.
ZM_RUN_AUDIT:
The zmaudit daemon exists to check that the saved information in the database and on the file system match and are consistent with each other. If an error occurs or if you are using 'fast deletes' it may be that database records are deleted but files remain. In this case, and similar, zmaudit will remove redundant information to synchronize the two data stores. This option controls whether zmaudit is run in the background and performs these checks and fixes continuously. This is recommended for most systems however if you have a very large number of events the process of scanning the database and file system may take a long time and impact performance. In this case you may prefer to not have zmaudit running unconditionally and schedule occasional checks at other, more convenient, times.
ZM_AUDIT_CHECK_INTERVAL:
The zmaudit daemon exists to check that the saved information in the database and on the files system match and are consistent with each other. If an error occurs or if you are using 'fast deletes' it may be that database records are deleted but files remain. In this case, and similar, zmaudit will remove redundant information to synchronize the two data stores. The default check interval of 900 seconds (15 minutes) is fine for most systems however if you have a very large number of events the process of scanning the database and file system may take a long time and impact performance. In this case you may prefer to make this interval much larger to reduce the impact on your system. This option determines how often these checks are performed.
What does a 'Can't shmget: Invalid argument' error in my logs mean? and my cameras won't display video at higher resolutions.
So, for example:
384x288 capture resolution, that makes: 110 592 pixels
in 24 bit color that's x24 = 2 654 208 bits per frame
by 80 frames ring buffer x80 = 212 336 640 bits per camera
by 4 cameras x4 = 849 346 560 bits.
Plus 10% overhead = 934 281 216 bits
That's 116 785 152 bytes, and
= 114 048 kB, respectively 111.38 MB.
If my shared memory is set to 134 217 728, which is exactly 128MB,
that means I shouldn't have any problem.
(Note that 1 byte = 8 bits and 1kbyte = 1024bytes, 1MB = 1024 kB)
If for instance you were using 24bit 640x480 then this would come to about 92Mb if you are using the default buffer size of 100. If this is too large then you can either reduce the image or buffer sizes or increase the maximum amount of shared memory available. If you are using RedHat then you can get details on how to change these settings at http://www.redhat.com/docs/manuals/database/RHDB-2.1-Manual/admin_user/kernel-resources.html .
You can often find out how many 4KB shared memory pages are available by typing the following :-
# cat /proc/sys/kernel/shmall
2097152
In recent kernels the shmall is set to 2097152 memory pages multiplied by 4096 bytes per page for a total of 8 GB of shared memory available. You only need to increase the shmall value if you have a computer with more than 8GB of memory and wish to use more of it for shared memory usage, such as large databases.
The most shared memory bytes you can allocate in one go :-
# cat /proc/sys/kernel/shmmax
33554432
In recent kernels the shmmax is set to 33554432 bytes for only 32 MB of maximum shared memory allocatable at a time, hardly enough for ZoneMinder to go above 320 x 240 x 24-bit resolution at 40 frames in the buffer if it is using the /dev/shm shared memory device, so this value needs to be increased. If you are using ZoneMinder with the memory mapped (mmap) compile time option then this doesn't affect you.
To change the value to 128 MB temporarily during this kernel execution type (for example) :-
Be sure to restart ZoneMinder after this. However be aware that sometimes you will only need to change the shmmax value as shmall is often large enough. Also changing these values in this way is only effective until your machine is rebooted.
To change them permanently you will need to edit /etc/sysctl.conf and add the following lines (for example) :-
kernel.shmmax = 536870912
Or if your distribution has the /etc/sysctl.d/ folder you can create a file in this folder without modifying the /etc/sysctl.d so you won't lose the changes during distro upgrades :-
echo kernel.shmmax = 536870912 >/etc/sysctl.d/60-kernel-shm.conf
To load these settings in the sysctl.conf file type:
sysctl -p
To check your shared memory settings type:
ipcs -l
Note that with Megapixel cameras like the Axis 207mw becoming cheaper and more attractive, the above memory settings are not adequate. To get Zoneminder working with a full 1280x1024 resolution camera in full color, increase 134217728 (128 MB) to, for example, 268435456 (256 MB) and multiple this value by each camera.
These changes will now also be set the next time your machine is restarted.
Versions 1.24.x of ZoneMinder also allows you to use an alternate method of shared memory allocation, mapped memory. This requires less configuration and can be simpler to use. Mapped memory allows you to use a special type of file as the placeholder for your memory and this file is 'mapped' into memory space for easy and fast access.
To enable mapped memory in ZoneMinder you need add add the --enable--mmap=yes switch to your configure line. By default mapped memory files are created in /dev/shm which on most distributions is a dedicated pseudo-partition containing memory formatted as a filesystem. If your system uses a different path then this can be changed in ZoneMinder in Options->paths->PATH_MAP. It uses a filesystem type called tmpfs. If you type 'df' you should see this area and the size of memory it currently allows. It is important that you do not use a disk based filesystem for your memory mapped files as this will cause memory access to be extremely slow. ZoneMinder creates files called .zm.mmap.<monitor id> in the mapped memory filesystem.
Mapped memory is subject to the same limitations in terms of total memory as using more traditional shared memory but does not require any configuration per allocation or chunk. In future versions of ZoneMinder this will be the default shared memory storage method.
Another good article about shared memory settings http://publib.boulder.ibm.com/infocenter/db2luw/v9/index.jsp?topic=/com.ibm.db2.udb.uprun.doc/doc/t0008238.htm . It made a statement that conflicted with those in the Redhat article but they fixed a long standing memory issue on FC6, so give them a try.
The essential difference was that the kernel.shmall setting is NOT in a direct memory setting in KB but in pages of memory. it is Max Pages of memory
For example: If you want to allocate a maximum memory setting to 8GB you have to convert it to the number of pages (or segments). with a page size of 4096.
  • kernel.shmall = 8000x1024x1024/4096
kernel.shmall = 2097152
NOT 8388608000 as would be suggested in the RedHat article linked above.
shmmax is the max amount to allocate in one request - this is is an actual memory size (as opposed to pages) set to 4GB
kernel.shmmax = 4294967296
The /etc/sysctl.conf would have these lines
As above, reload your sysctl.conf with sysctl -p and check that the settings are correct with ipcs -l.
I have enabled motion detection but it is not always being triggered when things happen in the camera view
ZoneMinder uses zones to examine images for motion detection. When you create the initial zones you can choose from a number of preset values for sensitivity etc. Whilst these are usually a good starting point they are not always suitable for all situations and you will probably need to tweak the values for your specific circumstances. The meanings of the various settings are described in the documentation (http://www.zoneminder.com/wiki/index.php/Documentation#Defining_Zones) however if you believe you have sensible settings configured then there are two diagnostic approaches you can use.
Event Statistics
The first technique is to use event statistics. Firstly you should ensure they are switched on in Options->Logging->RECORD_EVENT_STATS. This will then cause the raw motion detection statistics for any subsequently generated events to be written to the DB. These can then be accessed by first clicking on the Frames or Alarm Frames values of the event from any event list view in the web gui. Then click on the score value to see the actual values that caused the event. Alternatively the stats can be accessed by clicking on the 'Stats' link when viewing any individual frame. The values displayed there correspond with the values that are used in the zone configuration and give you an idea of what 'real world' values are being generated.
Note that if you are investigating why events 'do not' happen then these will not be saved and so won't be accessible. The best thing to do in that circumstance is to make your zone more sensitive so that it captures all events (perhap even ones you don't want) so you can get an idea of what values are being generated and then start to adjust back to less sensitive settings if necessary. You should make sure you test your settings under a variety of lighting conditions (e.g. day and night, sunny or dull) to get the best feel for that works and what doesn't.
Using statistics will slow your system down to a small degree and use a little extra disk space in the DB so once you are happy you can switch them off again. However it is perfectly feasible to keep them permanently on if your system is able to cope which will allow you to review your setting periodically.
Diagnostic Images
The second approach is to use diagnostic images which are saved copies of the intermediate images that ZM uses when determining motion detection. These are switched on and off using Options->Logging->RECORD_DIAG_IMAGES.
There are two kinds of diagnostic images which are and are written (and continuously overwritten) to the top level monitor event directory. If an event occurs then the files are additionally copied to the event directory and renamed with the appropriate frame number as a prefix.
The first set are produced by the monitor on the image as a whole. The diag-r.jpg image is the current reference image against which all individual frames are compared and the diag-d.jpg image is the delta image highlighting the difference between the reference image and the last analysed image. In this images identicial pixels will be black and the more different a pixel is the whiter it will be. Viewing this image and determining the colour of the pixels is a good way of getting a feel for the pixel differences you might expect (often more than you think).
The second set of diag images are labelled as diag-<zoneid>-<stage>.jpg where zoneid is the id of the zone in question (Smile) and the stage is where in the alarm check process the image is generated from. So if you have several zones you can expect to see multiple files. Also these files are only interested in what is happening in their zone only and will ignore anything else outside of the zone. The stages that each number represents are as follows,
  1. Alarmed Pixels - This image shows all pixels in the zone that are considered to be alarmed as white pixels and all other pixels as black.
  2. Filtered Pixels - This is as stage one except that all pixels removed by the filters are now black. The white pixels represent the pixels that are candidates to generate an event.
  3. Raw Blobs - This image contains all alarmed pixels from stage 2 but aggrageted into blobs. Each blob will have a different greyscale value (between 1 and 254) so they can be difficult to spot with the naked eye but using a colour picker or photoshop will make it easier to see what blob is what.
  4. Filtered Blobs - This image is as stage 3 but under (or over) sized blobs have been removed. This is the final step before determining if an event has occurred, just prior to the number of blobs being counted. Thus this image forms the basis for determining whether an event is generated and outlining on alarmed images is done from the blobs in this image.
Using the above images you should be able to tell at all stages what ZM is doing to determine if an event should happen or not. They are useful diagnostic tools but as is mentioned elsewhere they will massively slow your system down and take up a great deal more space. You should never leave ZM running for any length of time with diagnostic images on.
Why can't ZoneMinder capture images (either at all or just particularly fast) when I can see my camera just fine in xawtv or similar?
With capture cards ZoneMinder will pull images as fast as it possibly can unless limited by configuration. ZoneMinder (and any similar application) uses the frame grabber interface to copy frames from video memory into user memory. This takes some time, plus if you have several inputs sharing one capture chip it has to switch between inputs between captures which further slows things down.
On average a card that can capture at 25fps per chip PAL for one input will do maybe 6-10fps for two, 1-4fps for three and 1-2 for four. For a 30fps NTSC chip the figures will be correspondingly higher. However sometimes it is necessary to slow down capture even further as after an input switch it may take a short while for the new image to settle before it can be captured without corruption.
When using xawtv etc to view the stream you are not looking at an image captured using the frame grabber but the card's video memory mapped onto your screen. This requires no capture or processing unless you do an explicit capture via the J or ctrl-J keys for instance. Some cards or drivers do not support the frame grabber interface at all so may not work with ZoneMinder even though you can view the stream in xawtv. If you can grab a still using the grab functionality of xawtv then in general your card will work with ZoneMinder.
Why can't I see streamed images when I can see stills in the Zone window etc?
1) You are using Internet Explorer and are trying to view multi-part jpeg streams. IE does not support these streams directly, unlike most other browsers. You will need to install Cambozola or another multi-part jpeg aware pluging to view them. To do this you will need to obtain the applet from the Downloads page and install the cambozola.jar file in the same directly as the ZoneMinder php files. Then find the ZoneMinder Options->Images page and enable ZM_OPT_CAMBOZOLA and enter the web path to the .jar file in ZM_PATH_CAMBOZOLA. This will ordinarily just be cambozola.jar. Provided (Options / B/W tabs) WEB_H_CAN_STREAM is set to auto and WEB_H_STREAM_METHOD is set to jpeg then Cambozola should be loaded next time you try and view a stream.
NOTE: If you find that the Cambozola applet loads in IE but the applet just displays the version # of Cambozola and the author's name (as opposed to seeing the streaming images), you may need to chmod (-rwxrwxr-x) your (usr/share/zoneminder/) cambozola.jar:
2) The other common cause for being unable to view streams is that you have installed the ZoneMinder cgi binaries (zms and nph-zms) in a different directory than your web server is expecting. Make sure that the --with-cgidir option you use to the ZoneMinder configure script is the same as the CGI directory configure for your web server. If you are using Apache, which is the most common one, then in your httpd.conf file there should be a line like
where the last directory in the quotes is the one you have specified. If not then change one or the other to match. Be warned that configuring apache can be complex so changing the one passed to the ZoneMinder configure (and then rebuilding and reinstalling) is recommended in the first instance. If you change the apache config you will need to restart apache for the changes to take effect. If you still cannot see stream reliably then try changing Options->Paths->ZM_PATH_ZMS to just use zms if nph-zms is specified, or vice versa. Also check in your apache error logs.
I have several monitors configured but when I load the Montage view in FireFox why can I only see two? or, Why don't all my cameras display when I use the Montage view in FireFox?
By default FireFox only supports a small number of simultaneous connections. Using the montage view usually requires one persistent connection for each camera plus intermittent connections for other information such as statuses.
You will need to increase the number of allowed connections to use the montage view with more than a small number of cameras. Certain FireFox extensions such as FasterFox may also help to achieve the same result.
To resolve this situation, follow the instructions below:
Enter about:config in the address bar
scroll down to
browser.cache.check_doc_frequency 3
change the 3 to a 1
browser.cache.disk.enable True -> False
network.http.max-connections-per-server -> put a value of 100
network.http.max-persistent-connections-per-proxy -> 100 again
network.http.max-persistent-connections-per-server -> 100 again
There are a number of specific reasons why processor loads can be high either by design or by accident. To figure out exactly what is causing it in your circumstances requires a bit of experimentation.
The main causes are.
  1. Using a video palette other than greyscale or RGB24. This can cause a relatively minor performace hit, though still significant. Although some cameras and cards require using planar palettes ZM currently doesn't support this format internally and each frame is converted to an RGB representation prior to processing. Unless you have compelling reasons for using YUV or reduced RGB type palettes such as hitting USB transfer limits I would experiment to see if RGB24 or greyscale is quicker. Put your monitors into 'Monitor' mode so that only the capture daemons are running and monitor the process load of these (the 'zmc' processes) using top. Try it with various palettes to see if it makes a difference.
  2. Big image sizes. A image of 640x480 requires at least four times the processing of a 320x240 image. Experiment with different sizes to see what effect it may have. Sometimes a large image is just two interlaced smaller frames so has no real benefit anyway. This is especially true for analog cameras/cards as image height over 320 (NTSC) or 352 PAL) are invariably interlaced.
  3. Capture frame rates. Unless there's a compelling reason in your case there is often little benefit in running cameras at 25fps when 5-10fps would often get you results just as good. Try changing your monitor settings to limit your cameras to lower frame rates. You can still configure ZM to ignore these limits and capture as fast as possible when motion is detected.
  4. Run function. Obviously running in Record or Mocord modes or in Modect with lots of events generates a lot of DB and file activity and so CPU and load will increase.
  5. Basic default detection zones. By default when a camera is added one detection zone is added which covers the whole image with a default set of parameters. If your camera covers a view in which various regions are unlikely to generate a valid alarm (ie the sky) then I would experiment with reducing the zone sizes or adding inactive zones to blank out areas you don't want to monitor. Additionally the actual settings of the zone themselves may not be optimal. When doing motion detection the number of changed pixels above a threshold is examined, then this is filter, then contiguous regions are calculated to see if an alarm is generated. If any maximum or minimum threshold is exceeded according to your zone settings at any time the calculation stops. If your settings always result in the calculations going through to the last stage before being failed then additional CPU time is used unnecessarily. Make sure your maximum and minimumzone thresholds are set to sensible values and experiment by switching RECORD_EVENT_STATS on and seeing what the actual values of alarmed pixels etc are during sample events.
  6. Optimise your settings. After you've got some settings you're happy with then switching off RECORD_EVENT_STATS will prevent the statistics being written to the database which saves some time. Other settings which might make a difference are ZM_FAST_RGB_DIFFS, ZM_OPT_FRAME_SERVER and the JPEG_xxx_QUALITY ones.
This function has from time to time been corrupted in the SVN release or in the stable releases, try and reinstall from a fresh download.
How much Hard Disk Space / Bandwidth do I need for ZM?
Or go to this link for the Axis bandwidth calculator. Although this is aimed at Axis cameras it still produces valid results for any kind of IP camera.
As a quick guide I have 4 cameras at 320x240 storing 1 fps except during alarm events. After 1 week 60GB of space in the volume where the events are stored (/var/www/html/zm) has been used.
Many Linux distributions nowadays are built with security in mind. One of the latest methods of achieving this is via SELinux (Secure Linux) which controls who is able to run what in a more precise way then traditional accounting and file based permissions ([1]). If you are seeing entries in your system log like:
To Manage Users:
  • You may also consider to use the web server security, for example, htaccess files under Apache scope; You may even use this as an additional/redundant security on top of Zoneminders built-in security features;
Why does ZM stop recording once I have 32000 events for my monitor?
This is a limitation of the ext3 filesystem that most Linux distributions use. One directory cannot hold more than 32k approx files.
Version of ZM from 1.23.0 onwards allow you to have a deeper filesystem with fewer files per individual directory. As well as not being susceptible to the 32k limit this is also somewhat faster. However it is relatively and although few issues have been reported thus far it should be considered in beta for now. Also, it is currently not possible to migrate saved events between the different storage formats so is only suitable for new installations or if you do not mind losing saved events.
So if you do not want to use the deeper filesystem option (Options->Paths->ZM_USE_DEEP_STORAGE), for now you have to reduce the number of events or store your images (e.g. /var/lib/zoneminder) on a partition that uses a different filesystem such as ext4 or reiserfs.
You can read about the lack of a limit in the number of sub-directories in the ext4 filesystem at:
 http://kernelnewbies.org/Ext4
and see what tools may assist in your use of this filesystem in:
 http://ext4.wiki.kernel.org/index.php/Ext4_Howto
Note that while GParted 0.5.2 recognizes ext4 partitions, at least in some circumstances it does not succeed in formatting a partition for the ext4 filesystem. Also, if you search for ext3 or reiserfs on the forums you will find various threads on this issue with guidance on how to convert.
Managing system load (with IP Cameras in mind)
Introduction
Why do ZM need so much grunt? Think what Zoneminder is actually doing. In modect mode ZM is: 1. Fetching a jpeg from the camera. (Either in single part or multipart stream) 2. Decoding the jpeg image. 3. Comparing the zoned selections to the previous image or images and applying rules. 4. If in alarm state, writing that image to the disk and updating the mysql database.
How do I know if my computer is overloaded?
My load is too high, how can I reduce it?
Change the jpeg libraries. In most distributions Linux uses standard jpeg libraries which although fine for most things, don't use the MMX functions in nearly all modern processors. Check whether your cpu supports mmx by running "cpuid |grep MMX" which should give you a line or two along the lines of "MMX instructions". If so, give the libs a try. Most people report their load halves simply by using these libs. You may be able to experience substantial Zoneminder performance boosts now by merely upgrading your operating system, without having to download libraries and compile your own binaries, etc. as described in the forum thread linked below. Some distributions, e.g. Fedora 14 now include library code to utilize the instruction set extensions available in your processor:
 http://fedoraproject.org/wiki/Fedora_14_Alpha_release_notes#Faster_JPEG_Compression.2FDecompression
"The replacement of libjpeg with libjpeg-turbo brings speed improvements to a wide range of applications when handling images in JPEG format ..."
 http://fedoraproject.org/wiki/Releases/14/Schedule
still states "2010-11-02 final release".
CentOS 6.4 now has libjpeg-turbo built in as the default jpeg library allowing the best results out of the box.
 http://libjpeg-turbo.virtualgl.org/
provides some history on its project page. If you seek confirmation for which library is in use, you may consider querying e.g. while running on a prior distribution:
[u@who ~]$ rpm -q --whatprovides libjpeg
libjpeg-6b-46.fc12.i686
[u@who ~]$
and comparing the response to querying when the higher-performance library is available:
libjpeg-turbo-1.0.1-1.fc14.x86_64
[u@who ~]$
As noted in other forum postings, some zoneminder camera and usage configurations may not make much use of jpeg processing (e.g. some webcams), and thus obtain little performance benefit. Otherwise, you should be able to select one or more of:
  • running more cameras,
  • running existing cameras at higher image resolutions,
  • running cameras at a faster frame rate,
  • saving MoDect images with higher quality,
  • having more CPU cycles available for any non-Zoneminder workload, etc.
http://www.zoneminder.com/forums/viewtopic.php?t=6419 gives more info on the download-the-library-yourself, compile-your-own-Zoneminder binary, etc. approach if needed. Nobody's posted there to say it broke their system... Yet.
More expensive options:
Try building Zoneminder with processor specific instructions that are optimised to the system it will be running on, also increasing the optimisation level of GCC beyond -O2 will help.
./configure CFLAGS="-g -O3 -march=athlon-xp -mtune=athlon-xp" CXXFLAGS="-g -O3 -march=athlon-xp -mtune=athlon-xp"
The above command is optimised for an Athlon XP cpu so you will need to use the specific processor tag for your cpu, also the compiler optimisation has been increased to -O3.
You also need to put in your normal ./configure commands as if you were compiling with out this optimisation.
A further note is that the compile must be performed on the system that Zoneminder will be running on as this optimisation will make it hardware specific code.
Processor specific commands can be found in the GCC manual along with some more options that may increase performanc.
http://gcc.gnu.org/onlinedocs/gcc/i386-and-x86_002d64-Options.html#i386-and-x86_002d64-Options
The below command has been used to compile Zoneminder on a Athlon XP system running CentOS 5.5 and along with the libjpeg-turbo modification to reduce the CPU load in half, libjpeg-turbo reduced the load by 1/3 before the processor optimisation.
./configure --with-webdir=/var/www/html/zm --with-cgidir=/var/www/cgi-bin CFLAGS="-g -O3 -march=athlon-xp -mtune=athlon-xp" CXXFLAGS="-D__STDC_CONSTANT_MACROS -g -O3 -march=athlon-xp -mtune=athlon-xp" --enable-mmap --sysconfdir=/etc/zm
The following command has been used to compile Zoneminder 1.25 on a CentOS 6.0 system, the native command should choose the processor automatically during compile time, this needs to be performed on the actual system!!.
CFLAGS="-g -O3 -march=native -mtune=native" CXXFLAGS="-D__STDC_CONSTANT_MACROS -g -O3 -march=native -mtune=native" ./configure  --with-webdir=/var/www/html/zm --with-cgidir=/var/www/cgi-bin --with-webuser=apache --with-webgroup=apache ZM_DB_HOST=localhost ZM_DB_NAME=zm ZM_DB_USER=your_zm_user ZM_DB_PASS=your_zm_password ZM_SSL_LIB=openssl
What about disks and bandwidth?
Building ZoneMinder
When running configure I am getting a lot of messages about not being able to compile the ffmpeg libraries
If you see output from configure that looks like this
checking libavcodec/avcodec.h usability... no
checking libavcodec/avcodec.h presence... yes
configure: WARNING: libavcodec/avcodec.h: present but cannot be compiled
configure: WARNING: libavcodec/avcodec.h:     check for missing
prerequisite headers?
configure: WARNING: libavcodec/avcodec.h: see the Autoconf documentation
configure: WARNING: libavcodec/avcodec.h:     section "Present But
Cannot Be Compiled"
configure: WARNING: libavcodec/avcodec.h: proceeding with the compiler's
result
configure: WARNING:     ## ------------------------------------- ##
configure: WARNING:     ## Report this to support@zoneminder.com ##
then it is caused not by the ZoneMinder build system but ffmpeg itself. However there is a workaround you can use which is to add
 CPPFLAGS=-D__STDC_CONSTANT_MACROS
to the ZoneMinder ./configure command which should solve the issue. However this is not a proper 'fix' as such, which can only come from the ffmpeg project itself.
I cannot build ZoneMinder and am getting lots of undefined C++ template errors
This is almost certainly due to the 'ccache' package which attempts to speed up compilation by caching compiled objects. Unfortunately one of the side effects is that it breaks the GNU g++ template resolution method that ZoneMinder uses in building by prevent files getting recompiled. The simplest way around this is to remove the ccache package using your distros package manager.
How do I build for X10 support?
perl -MCPAN -eshell
install X10::ActiveHome
quit
Extending ZoneMinder
How can I get ZM to do different things at different times of day or week?
Now you can switch between these two states by selecting them from the same dialog you saved them, or from the command line from issue the command zmpkg.pl <run state>, for example zmpkg.pl Daytime.
The final step you need to take, is scheduling the time the changes take effect. For this you can use cron. A simple entry to change to the Daylight state at at 8am and to the nighttime state at 8pm would be as follows,
0 8 * * * root /usr/local/bin/zmpkg.pl Daytime
0 20 * * * root /usr/local/bin/zmpkg.pl Nighttime
On Ubuntu 7.04 and possibly others, look in /usr/bin not just /usr/local/bin for the zmpkg.pl file.
For an alternative method of time controlling ZoneMinder, forum user 'voronwe' has created a more interactive calendar style integration. Details of this can be found in this forum thread. If you would like to find out more about this contribution please post on this thread.
How can I use ZoneMinder to trigger something else when there is an alarm?
ZoneMinder includes a perl API which means you can create a script to interact with the ZM shared memory data and use it in your own scripts to react to ZM alarms or to trigger ZM to generate new alarms. Full details are in the README or by doing 'perldoc ZoneMinder', 'perldoc ZoneMinder::SharedMem' etc. Below is an example script that checks all monitors for alarms and when one occurs, prints a message to the screen. You can add in your own code to make this reaction a little more useful.
#!/usr/bin/perl -w
use strict;
use ZoneMinder;
$| = 1;
my $sql = "select M.*, max(E.Id) as LastEventId from Monitors as M left join Events as E on M.Id = E.MonitorId where M.Function != 'None' group by (M.Id)";
my @monitors;
    push( @monitors, $monitor );
while( 1 )
        next if ( !zmMemVerify( $monitor ) );
            # Do your stuff here
    sleep( 1 );
Trouble Shooting
ZoneMinder creates its own logs and are usually located in the /tmp directory.
The ZoneMinder logs for the RPM packages are located in /var/log/zm.
Depending on your problem errors can show up in any of these logs but, usually the logs of interest are zmdc.log and zmpkg.log if ZM is not able to start.
Now since ZM is dependent on other components to work, you might not find errors in ZM but in the other components. Other logs of interest are:
  • /var/log/messages and/or /var/log/syslog
  • /var/log/dmesg
  • /var/log/httpd/error_log (RedHat/Fedora) or /var/log/apache2/error_log
  • /var/log/mysqld.log (Errors here don't happen very often but just in case)
This will append any data entered to any of these logs to your console screen (-f). To exit, hit [ctrl -c].
More verbose logging for the ZoneMinder binaries is available by enabling the debug option from the control panel and will be placed in the path you have configured for the debug logs. Output can be limited to a specific binary as described in the Debug options page under the "?" marks.
How can I trouble shoot the hardware and/or software?
  • lspci -vv -- Returns lots of detailed info. Check for conflicting interrupts or port assignments. You can sometimes alter interrupts/ ports in bios. Try a different pci slot to get a clue if it is HW conflict (comand provided by the pciutils package).
  • scanpci -v -- Gives you information from your hardware EPROM
  • lsusb -vv -- Returns lots of detail about USB devices (camand provided by usbutils package).
  • dmesg -- Shows you how your hardware initialized (or didn't) on boot-up. You will get the most use of this.
  • v4l-info -- to see how driver is talking to card. look for unusual values.
  • modinfo bttv -- some bttv driver stats.
  • zmu -m 0 -q -v -- Returns various information regarding a monitor configuration.
  • ipcs -- Provides information on the ipc facilities for which the calling process has read acccess.
  • ipcrm -- The ipcrm command can be used to remove an IPC object from the kernel.
  • cat /proc/interrupts -- This will dispaly what interrupts your hardware is using.
Why is it that when monitoring a camera, the top portion of the image is cutoff and appears at the bottom of the image, with a line seperating the top from the bottom?
Why am I getting a 403 access error with my web browser when trying to access http //localhost/zm?
The apache web server needs to have the right permissions and configuration to be able to read the Zoneminder files. Check the forums for solution, and edit the apache configuration and change directory permissions to give apache the right to read the Zoneminder files. Depending on your Zoneminder configuration, you would use the zm user and group that Zoneminder was built with, such as wwwuser and www.
Why am I getting broken images when trying to view events?
Zoneminder and the Apache web server need to have the right permissions. Check this forum topic and similar ones: http://www.zoneminder.com/forums/viewtopic.php?p=48754#48754
Why is the image from my color camera appearing in black and white?
This may occur if you have a NTSC analog camera but have configured the source in ZoneMinder as PAL for the Device Format under the source tab. You may also be mislead because zmu can report the video port as being PAL when the camera is actually NTSC. Confirm the format of your analog camera by checking it's technical specifications, possibly found with the packaging it came in, on the manufacturers website, or even on the retail website where you purchased the camera. Change the Device Format setting to NTSC and set it to the lowest resolution of 320 x 240. If you have confirmed that the camera itself is NTSC format, but don't get a picture using the NTSC setting, consider increasing the shared memory kernel.shmall and kernel.shmmax settings in /etc/sysctl.conf to a larger value such as 268435456. This is also the reason you should start with the 320x240 resolution, so as to minimize the potential of memory problems which would interfere with your attempts to troubleshoot the device format issue. Once you have obtained a picture in the monitor using the NTSC format, then you can experiment with raising the resolution.
Why do I only see blue screens with a timestamp when monitoring my camera?
If this camera is attached to a capture card, then you may have selected the wrong Device Source or Channel when configuring the monitor in the ZoneMinder console. If you have a capture card with 2 D-sub style inputs(looks like a VGA port) to which you attach a provided splitter that splits off multiple cables, then the splitter may be attached to the wrong port. For example, PV-149 capture cards have two D-sub style ports labeled as DB1 and DB2, and come packaged with a connector for one of these ports that splits into 4 BNC connecters. The initial four video ports are available with the splitter attached to DB1.
Why do I only see black screens with a timestamp when monitoring my camera?
In the monitor windows where you see the black screen with a timestamp, select settings and enter the Brightness, Contrast, Hue, and Color settings reported for the device by zmu -d <device_path> -q -v. 32768 may be appropriate values to try for these settings. After saving the settings, select Settings again to confirm they saved successfully.
I am getting messages about a backtrace in my logs, what do I do?
Jan 11 20:25:22 localhost zma_m2[19051]: ERR [Backtrace: /lib64/libc.so.6 [0x3347230210]]
Jan 11 20:25:22 localhost zma_m2[19051]: ERR [Backtrace: /lib64/libc.so.6(memset+0xce) [0x334727684e]]
Jan 11 20:25:22 localhost zma_m2[19051]: ERR [Backtrace: /usr/local/bin/zma [0x40ee9a]]
Jan 11 20:25:22 localhost zma_m2[19051]: ERR [Backtrace: /usr/local/bin/zma [0x419946]]
Jan 11 20:25:22 localhost zma_m2[19051]: ERR [Backtrace: /usr/local/bin/zma [0x4213cf]]
Jan 11 20:25:22 localhost zma_m2[19051]: ERR [Backtrace: /usr/local/bin/zma(cos+0x35c) [0x404674]]
Jan 11 20:25:22 localhost zma_m2[19051]: ERR [Backtrace: /lib64/libc.so.6(__libc_start_main+0xf4) [0x334721da44]]
Jan 11 20:25:22 localhost zma_m2[19051]: ERR [Backtrace: /usr/local/bin/zma(cos+0xd1) [0x4043e9]]
Jan 11 20:25:22 localhost zma_m2[19051]: INF [Backtrace complete]
then you can help diagnose the problem by running a special command to translate the hex addresses into helpful information. This command is called addr2line and you can type 'man addr2line' for more information. Basically addr2line takes two sets of parameters, the first is the name of the binary file, and the second is a list of addresses. Both of these pieces of information are displayed in the logs. The filename is the first part after the 'Backtrace:' tag, in this case /usr/local/bin/zma, though it may well be different in your case. Some of the lines refer to libraries rather than the zma executable but those can be ignored for now, the important part is noting which ZM binary is involved. The binary file is passed in following the -e flag. The addresses to pass to addr2line are those contained in the '[]' pairs. Again you can ignore those that are on a line that refers to a library but it will not hurt if you include them.
So in the example above, the command would be
addr2line -e /usr/local/bin/zma 0x40ee9a 0x419946 0x4213cf 0x404674 0x4043e9
This error some times happens when a linked camera looses its link or it is corrupted by the user or some other system event, try deleting the affected cameras and recreating them in the Zoneminder console.
How do I repair the MySQL Database?
  • mysqlcheck --all-databases --auto-repair -pyour_database_password -u your_databse_user
  • myisamchk --silent --force --fast --update-state -O key_buffer=64M -O sort_buffer=64M -O read_buffer=1M -O write_buffer=1M /var/lib/mysql/*/*.MYI
How do I repair the MySQL Database when the cli fails?
In Ubuntu, the commands listed above do not seem to work. However, actually doing it by hand from within MySQL does. (But that is beyond the scope of this document) But that got me thinking... And phpmyadmin does work. Bring up a terminal.
sudo apt-get install phpmyadmin
Now go to http://zoneminder_IP/ and stop the ZM service. Continue to http://zoneminder_IP/phpmyadmin and select the zoneminder database. Select and tables marked 'in use' and pick the action 'repare' to fix. Restart the zoneminder service from the web browser. Remove or disable the phpmyadmin tool, as it is not always the most secure thing around, and opens your database wide to any skilled hacker.
sudo apt-get remove phpmyadmin
  1. /usr/local/bin/zmfix: /usr/lib/libmysqlclient.so.15: version `MYSQL_5.0' not found (required by /usr/local/bin/zmfix)  :: Solution: Recompile and reinstall Zoneminder.
Zoneminder doesn't start automatically on boot
Check the list for log entries like "zmfix[766]: ERR [Can't connect to server: Can't connect to local MySQL server through socket '/var/run/mysqld/mysqld.sock' (2)] ". What can happen is that zoneminder is started too quickly after Mysql and tries to contact the database server before it's ready. Zoneminder gets no answer and aborts. August 2010 - Ubuntu upgrades seem to be leaving several systems in this state. One way around this is to add a delay to the zoneminder startup script allowing Mysql to finish starting. "Simply adding 'sleep 15' in the line above 'zmfix -a' in the /etc/init.d/zoneminder file fixed my ZoneMinder startup problems!" - credit to Pada.
Remote Path setup for Panasonic and other Camera
On adding or editing the source you can select the preset link for the parameters for the specified camera . In version 1.23.3 presets for BTTV,Axis,Panasonic,GadSpot,VEO, and BlueNet are available . Selecting the presets ZM fills up the required value for the remote path variable
Why do I get repeated/ mixed/unstable/ blank monitors on bt878-like cards (a.k.a. PICO 2000)
Please have a check at Pico2000;
What causes "Invalid JPEG file structure: two SOI markers" from zmc (1.24.x)
Some settings that used to be global only are now per camera. On the Monitor Source tab, if you are using Remote Protocol "HTTP" and Remote Method "Simple", try changing Remote Method to "Regexp".
Miscellaneous
I see ZoneMinder is licensed under the GPL. What does that allow or restrict me in doing with ZoneMinder?
The ZoneMinder license is described at the end of the documentation and consists of the following section
This program is free software; you can redistribute it and/or modify it under the terms of the GNU General Public License as
published by the Free Software Foundation; either version 2 of the License, or (at your option) any later version.
This program is distributed in the hope that it will be useful, but WITHOUT ANY WARRANTY; without even the implied warranty
of MERCHANTABILITY or FITNESS FOR A PARTICULAR PURPOSE. See the GNU General Public License for more details.
This means that ZoneMinder is licensed under the terms described here. There is a comprehensive FAQ covering the GPL at http://www.gnu.org/licenses/gpl-faq.html but in essence you are allowed to redistribute or modify GPL licensed software provided that you release your distribution or modifications freely under the same terms. You are allowed to sell systems based on GPL software. You are not allowed to restrict or reduce the rights of GPL software in your distribution however. Of course if you are just making modifications for your system locally you are not releasing changes so you have no obligations in this case. I recommend reading the GPL FAQ for more in-depth coverage of this issue.
Can I use ZoneMinder as part of my commercial product?
The GPL license allows you produce systems based on GPL software provided your systems also adhere to that license and any modifications you make are also released under the same terms. The GPL does not permit you to include ZoneMinder in proprietary systems (see http://www.gnu.org/licenses/gpl-faq.html#GPLInProprietarySystem for details). If you wish to include ZoneMinder in this kind of system then you will need to license ZoneMinder under different terms. This is sometimes possible and you will need to contact me for further details in these circumstances.